A field survey on 36 old high‐rise buildings in the Hong Kong Special Administrative Region (HKSAR, formerly Hong Kong) was conducted to study the problems of the retrofit installation of sprinkler systems in those buildings. The floor plan, occupancy type, number of occupants, fire load distribution, hazard class, number of sprinklers to protection area ratio and the number of sprinkler heads were studied along with the characteristics of the buildings identified. A detailed investigation was carried out in an old high‐rise non‐residential building with sprinkler system installed. It was observed that the retrofit sprinkler systems might not perform satisfactorily in case of fire. Further, water discharged might not reach the ground level because the sprinkler sprays pattern was not considered. Technical and financial difficulties of installing sprinkler systems in old high‐rise buildings were studied. In addition, it was ascertained that problems related to structural loading for the system, variation in the occupancy level, allocating spaces for the sprinkler system components such as water tank, pumps and pipes compound the complexity of installing sprinkler systems in old high‐rise buildings. Finally, the cost for retrofit sprinkler installation has been estimated.
Article navigation
1 March 1999
Research Article|
March 01 1999
Problems of the retrofit installation of sprinkler systems in old high‐rise buildings: a case study
W.K. Chow;
W.K. Chow
The Department of Building Services Engineering at the Hong Kong Polytechnic University, Hong Kong, China
Search for other works by this author on:
H.W. Chong;
H.W. Chong
The Department of Building Services Engineering at the Hong Kong Polytechnic University, Hong Kong, China
Search for other works by this author on:
L.T. Wong
L.T. Wong
The Department of Building Services Engineering at the Hong Kong Polytechnic University, Hong Kong, China
Search for other works by this author on:
Publisher: Emerald Publishing
Online ISSN: 1758-7131
Print ISSN: 0263-2772
© MCB UP Limited
1999
Facilities (1999) 17 (3-4): 112–119.
Citation
Chow W, Chong H, Wong L (1999), "Problems of the retrofit installation of sprinkler systems in old high‐rise buildings: a case study". Facilities, Vol. 17 No. 3-4 pp. 112–119, doi: https://doi.org/10.1108/02632779910256533
Download citation file:
New and popular articles
Suggested Reading
But is fire the issue …? The problems of managing multiple ownership buildings in Hong Kong
Property Management (December,1998)
Fire safety legislation in Hong Kong
Facilities (September,1998)
Decommissioning deadline for Halon fire extinguishing systems
Facilities (January,2000)
Fires in Construction Industry Escalate
Facilities (December,1998)
Fire Responsibilities
Facilities (December,1998)
Related Chapters
FIRE PROTECTION CONCEPTS FOR TRAFFIC TUNNELS: LATEST DEVELOPMENTS AND RECENT RESEARCH ACTIVITIES
Concrete for Transportation Infrastructure: Proceedings of the International Conference held at the University of Dundee, Scotland, UK on 5–7 July 2005
THE PRODUCTION AND USE OF CEMENT IN A SUSTAINABLE CONTEXT
Role of Cement Science in Sustainable Development: Proceedings of the International Symposium held at the University of Dundee, Scotland, UK on 3–4 September 2003
The Behavior of Hong Kong Cross-Border Shoppers: A Nonparametric Approach
Advances in Hospitality and Leisure
Recommended for you
These recommendations are informed by your reading behaviors and indicated interests.