Article navigation

The authors have produced some useful experimental data on the heat evolution of concrete mixes containing different mineral admixtures (Ramu et al., 2016). These data may be further analysed for deeper study.

For the ordinary Portland cement (OPC) concrete, it is observed that the heat evolution was not directly proportional to the cement content, as listed in Table 6, where it can be seen that the total heat varied from 245 kJ/kg at a water to cement (w/c) ratio of 0·38 to 256 kJ/kg at a w/c ratio of 0·45. Such variation may be attributed to the incomplete degree of hydration, which is dependent on the w/c ratio, as has been found in previous studies by the discussers (Ng et al., 2008, 2009).

Table 6.

Total heat evolution of OPC concrete

MixWater content: kg/m3Cement content: kg/m3w/c ratioTotal heat: kJ/kg
C2-M30-11713800·45256
C2-M30-61533600·43250
C2-M50-31804700·38245

For the fly ash concrete, it is evident from the results listed in Table 7 that the total heat was generally lower at a higher fly ash replacement ratio and/or a lower water to binder (w/b) ratio. Again, the lower total heat at lower w/b ratio and higher total heat at higher w/b ratio may be attributed to the difference in degree of chemical reactions at different w/b ratios, as has been reported previously by the discussers (Kwan et al., 2011a). The placing temperature might have also affected the total heat, but the placing temperature results have not been given in the paper.

Table 7.

Total heat evolution of fly ash concrete

MixFly ash replacement ratioBinder content: kg/m3w/b ratioTotal heat: kJ/kg
C2-M30-20·254000·45274
C2-M30-30·213800·43277
C2-M30-40·384500·39219
C2-M30-50·254800·47207
C2-M30-70·173600·50377
C2-M30-80·294500·42190
C2-M30-90·274600·49226

For the silica fume concrete, for which the results are summarised in Table 8, it is particularly interesting to note that the addition of 5% silica fume has reduced the total heat by 8·0%, whereas the addition of 10% silica fume has reduced the total heat by 10·3%. Hence, the percentage reduction in heat evolution was larger than the percentage reduction in cement content. A similar phenomenon was observed by the discussers in a previous study (Kwan et al., 2011b). Further research is recommended to explain this phenomenon.

Table 8.

Total heat evolution of silica fume concrete

MixSilica fume replacement ratioBinder content: kg/m3w/b ratioTotal heat: kJ/kg
C1-M80-P04300·35261
C1-M80-MA10·054300·35240
C1-M80-MA20·104300·35234

The authors thank Dr Kwan and Dr Ng for their insightful discussion of this paper. Indeed, the extent of the chemical reactions at different w/b ratios is expected to have an effect on the heat evolved. However, the authors wish to clarify that this was not a parametric study; rather, they analysed only heat evolution from concretes with mixture designs that are used commercially. Further, as rightly pointed out, additional work is necessary to understand the reduction in heat evolution with silica fume concrete, particularly also considering the influence of the particle size of the material.

Kwan
AKH
,
Fung
WWS
,
Chen
JJ
and
Ng
PL
(
2011a
)
Heat generation of curing fly ash concrete at different w/cm
.
ACI Materials Journal
108
(
3
):
307
315
.
Kwan
AKH
,
Chen
JJ
,
Fung
WWS
and
Ng
PL
(
2011b
)
Effects of silica fume on heat generation of curing concrete
.
ACI Materials Journal
108
(
6
):
655
663
.
Ng
PL
,
Ng
IYT
and
Kwan
AKH
(
2008
)
Heat loss compensation in semi-adiabatic curing test of concrete
.
ACI Materials Journal
105
(
1
):
52
61
.
Ng
IYT
,
Ng
PL
and
Kwan
AKH
(
2009
)
Effects of cement and water contents on adiabatic temperature rise of concrete
.
ACI Materials Journal
106
(
1
):
42
49
.
Ramu
YK
,
Akhtar
I
and
Santhanam
M
(
2016
)
Use of adiabatic calorimetry for performance assessment of concretes
.
Advances in Cement Research
28
(
8
):
485
493
, .

or Create an Account

Close subscription notice
Close access options