This paper presents a finite element model highlighting the behaviour of bonded post-tensioned one-way spanning concrete slabs in fire conditions. The model was verified against ten fire tests on bonded post-tensioned concrete slabs at ambient and elevated temperatures. The slabs were simply supported and post-tensioned with 15·7 mm nominal diameter seven-wire mono-strand tendons. The mechanical and thermal material non-linearities of the entire slab’s components, consisting of the concrete, plastic and galvanised steel ducts, prestressing tendon and the anchorages, have been carefully inserted into the model. The interface between the tendon and surrounding grout was also considered, allowing the bond behaviour to be modelled and the tendon to retain its profile shape during the deformation of the slab. The temperature distributions throughout the slab, together with the slab’s development of displacement and stress, as it was heated, were predicted by the model and verified against test data. A parametric study was conducted to investigate the effects on the global structural behaviour owing to the change in the aggregate type, duct type, load ratio, boundary conditions and different fire scenarios. The study has shown that the bonded post-tensioned concrete slabs investigated in this study are capable of achieving the designed 90 min fire resistance. It is also shown that the fire resistance given by BS 8110-2 and BS EN 1992-1-2 are acceptable for the design of bonded post-tensioned one-way spanning concrete slabs under fire conditions.
Article navigation
December 2008
Research Article|
December 01 2008
Modelling of bonded post-tensioned concrete slabs in fire
E. A. M. Ellobody, PhD, CEng;
E. A. M. Ellobody, PhD, CEng
Associate Professor
Department of Structural Engineering, Tanta University
Egypt
Search for other works by this author on:
C. G. Bailey, PhD, CEng, FICE, MIStructE, MIFireE
C. G. Bailey, PhD, CEng, FICE, MIStructE, MIFireE
Professor and Head of School of Mechanical
Aerospace and Civil Engineering, The University of Manchester
UK
Search for other works by this author on:
Publisher: Emerald Publishing
Received:
May 13 2008
Accepted:
August 19 2008
Online ISSN: 1751-7702
Print ISSN: 0965-0911
© 2008 Thomas Telford Ltd
2008
Proceedings of the Institution of Civil Engineers - Structures and Buildings (2008) 161 (6): 311–323.
Article history
Received:
May 13 2008
Accepted:
August 19 2008
Citation
Ellobody EAM, Bailey CG (2008), "Modelling of bonded post-tensioned concrete slabs in fire". Proceedings of the Institution of Civil Engineers - Structures and Buildings, Vol. 161 No. 6 pp. 311–323, doi: https://doi.org/10.1680/stbu.2008.161.6.311
Download citation file:
New and popular articles
Suggested Reading
Editorial
Proceedings of the Institution of Civil Engineers - Structures and Buildings (September,2014)
Discussion: Partially and non-destructive testing of 40 concrete bridges
Proceedings of the Institution of Civil Engineers - Structures and Buildings (February,2002)
Editorial
Proceedings of the Institution of Civil Engineers - Structures and Buildings (February,2006)
Editorial
Proceedings of the Institution of Civil Engineers - Structures and Buildings (November,2002)
Elsewhere in ICE Proceedings
Proceedings of the Institution of Civil Engineers - Structures and Buildings (February,2005)
Related Chapters
Types of berth structures
Port Designer's Handbook
Gravity wall structures
Port Designer's Handbook
Sheet pile wall structures
Port Designer's Handbook
Recommended for you
These recommendations are informed by your reading behaviors and indicated interests.